Bosch · Heat pump

F2 System lockout (5 low-pressure trips in 100 minutes)

High severity Bosch IDS LightBosch IDS Premium Connected

What the control is telling you

The unit locked out after repeated low-pressure protection (P21/P2). A hard restart is required.

Applies to: Bosch IDS Light BOVA15-24/36/60 and IDS Premium Connected BOVA36-20/60-20 R-454B heat pump outdoor units

Likely causes

  • Closed service valves
  • Undercharge
  • Blockage or poor heat exchange
  • Failed transducer

Test and repair steps

  1. Fix the cause of the low-pressure trips (see P21).
  2. Hard restart the system after repair.

Models that show this code

5 models in Bosch IDS Light, Bosch IDS Premium Connected

BOVA15-24BOVA15-36BOVA15-60BOVA36-20BOVA60-20

Other codes on the same units

  • E51 Input voltage out of range
  • E52 DC bus voltage out of range
  • E81 EEV coil fault
  • F1 High pressure switch protection
  • F4 Pressure transducer fault
  • F41 High pressure sensor fault
  • F42 Low pressure sensor fault
  • H01 Drive chip communication fault

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Bosch IDS Light installation BTC 762003308 D (02.2025), Fault Code Table 23 and 17.12 Error Code Troubleshooting, p.42-59; Bosch IDS Premium Connected installation BTC 762003301 D (02.2025), Fault Code Table 22 and 18.12 Error Code Troubleshooting. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.