Bosch · Heat pump

F42 Low pressure sensor fault

Medium severity Bosch IDS LightBosch IDS Premium Connected

What the control is telling you

The low-side pressure sensor signal is faulty.

Applies to: Bosch IDS Light BOVA15-24/36/60 and IDS Premium Connected BOVA36-20/60-20 R-454B heat pump outdoor units

Likely causes

  • Loose CN15 wiring
  • Failed transducer
  • Control board

Test and repair steps

  1. Check the CN15 connection for damage.
  2. Replace the transducer, then the control board if it persists.

Models that show this code

5 models in Bosch IDS Light, Bosch IDS Premium Connected

BOVA15-24BOVA15-36BOVA15-60BOVA36-20BOVA60-20

Other codes on the same units

  • F1 High pressure switch protection
  • F2 System lockout (5 low-pressure trips in 100 minutes)
  • F4 Pressure transducer fault
  • F41 High pressure sensor fault
  • H01 Drive chip communication fault
  • J00-JCF Compressor driver fault
  • n00-nCF Outdoor fan motor driver fault
  • o37 Low refrigerant in heating

Save it for the next call

Star this code in the HVACopedia app and keep the whole library on your phone for jobs with no signal.

Open the app

Source: Bosch IDS Light installation BTC 762003308 D (02.2025), Fault Code Table 23 and 17.12 Error Code Troubleshooting, p.42-59; Bosch IDS Premium Connected installation BTC 762003301 D (02.2025), Fault Code Table 22 and 18.12 Error Code Troubleshooting. Summarized in our own words; check the original manual for your model.

Homeowner looking at this code? See what it means for you and when to call a technician.

For licensed technicians. Gas, electrical and refrigerant work must be done by a qualified, licensed person. Shut off power and gas before servicing, never bypass a safety control, and follow the manufacturer’s manual for the exact model; it and local codes always take priority. HVACopedia is not affiliated with any manufacturer; brand and model names only identify the equipment.